Unfortunately, we have not managed yet to implement the EIB:

We have installed the replaced EIB/UCM and we have set it up for a 3-level group address (Main Group 1, Mid Group 0 to 3 and subgroup 0-31) by setting the shunts as follows: SW8A Short, SW8B Open, SW8C Open, SW8D Closed.

When a switch within the range of above addresses (e.g. 1/1/3) is activated the D2 (BUSY1) blinks so we assume it correctly registers an incoming telegram.

The D9 & D10 blink so RS485 seems o.k.

Sometimes the ERROR LED lights up and after a while it goes off. Usually it does that when a switch is activated which is not in the range of addresses. Is this normal?

We have not managed to send a telegram. We used both WizComfor and Comfigurator to EXECUTE an EIB response but nothing. We also linked an EIB response to an Input Zone but again no telegram was sent. The D3 never blinked.

Any suggestions please?

Thanks