In Non Detector Alarms you have changed the assignment of ND alarm 0 from Intruder to Alert, see below screenshot. 

This causes the problem that you experienced.

Non detector alarms should not be changed, as they affect the behaviour of the alarm, unless you know exactly whet is the effect   


Please revert all NonDetector alarms to the original setting. Open a new file Comfort 2 Ultra to compare the original settings.

Zone Types assignment should also not be changed unless you are very sure of what the effect will be. 

This is regardless of the Firmware 7,183 or other older versions.