You write that the compiler supports custom applications. But there can be problems in the c-bus network with these groups...
I tested the transfer of these groups on the network, via the touch screen, the group changed and transmitted within the network.
Problems occur on your device during transmission from c-bus network to knx.
For testing, I used the following tools:
For c-bus network: USB conection to network (5500PACA) and C-bus Toolkit v.1.14.6- --- 
For KNX network: TCP/IP connection to WEB interface of Logic Machine 5 (Openrb)
For Cytech c-bus knx translator: USB connection and Bus Translator Configurator v.1.0.1.0 (config in attachment)



In this video I use only group Lighting applications (56). Transmission in both directions is operating normally.
https://youtu.be/fVh3c1QOEk4

In this video I use the application 49. It is evident that the group is transferred to the c-bus network. Even in the logs of your device can be seen that from a c-bus network comes status changes of this group.But changes dont transmit to KNX network.
https://youtu.be/0cLSgiX23mg

Custom application groups has type like groups in Lighting (56) application. And can be set ON, OFF, or ramped from 0 to 255. 