Known Issues
  1. In Flags screen, if Check Status box is checked for a flag, the status is updated, but if the flag changes subsequently, the flag status in the centre pane is not updated until you go to another page and back, or uncheck and check the box (old bug)
  2. In Modbus configurator, Sensors cannot be mapped to Modbus
  3. for TSM, if older firmware eg TSM 7.001 has read from EEPROM, this may cause  an exception. Workaround is to upgrade TSM to  the latest (7.003) firmware first
Bugs Fixed
  1. "If Input" comparison action did not work for Input > 64 to 96. This also applies for older versions
  2. Deg C /deg F in Comfiguration flags is incorrect
  3. Comfort Optimum when adding  UCM/KNX2 caused exception
  4. Read from KP06A or KP04A does not change the KP06A/KP04A settings  in Comfigurator
  5. IRIO IR codes do not refresh when new IR codes are learned. Refresh button is needed
  6. Default template def40.cctx for UCM/Logic is missing from the installation.
  7. Export Scenario dis not work. Selecting any items will cause an exception
New Features
TSM01
  1. Added parameters; Heating / Cooling Mode, Virtual Input, Heating/Cooling Output, Virtual Alarm Offset, Calibration Offset. This implements the Temperature Alarm Monitoring feature which maps to Virtual Input to trigget the Temperature Alarm. New Temperature Alarm Type, TempNO Zone Type added to defaults.
HIO
  1. Added Lighting Sequence Timer Parameter for delay between each light turning off in Occupancy Detection Mode
IRIO
  1. Added Resistive Sensor Input Functions
UCM/Modbus
Supports the new UCM/Modbus. New Product will be announced soon





Last edited on Sunday Dec 4th, 2016 11:24 am by slychiu