And here is my twist on all this. I set my PC to NTP time, set Comfort to be +-1 minute out from NTP time and then waited. I started to monitor at 13:19 and the Time Change came through at 14:01. Firstly it didn't come within the 10 minutes my Eth03 was configured for and secondly it didn't set Comfort time at all.
09 May 2015
13: 19: 33: 961 ----< 03 00 9A 31 34 30 30 30 31 34 45 02 <--->/š1400014E
broadcast for flag:14state is:00
14: 01: 26: 359 ----< 03 00 53 32 30 31 35 30 35 30 39 31 34 30 30 30 30 30 30 35 33 02 <--->/S201505091400000053
Set date and time
|
The time on Comfort is confirmed to be that same +-1 minute out even after the Time Change update. Looking at the event log I should see a time change event at 14:01 right? Nothing, nada, zip. No Date Time change in the event log even though the Bus monitor shows a Set command.