View single post by slychiu | |||||||||||||
---|---|---|---|---|---|---|---|---|---|---|---|---|---|
Posted: Wednesday Feb 25th, 2015 06:24 am |
|
||||||||||||
slychiu
|
Can you confirm that the KT03 buttons are able to work for the keypad key and arming page and Panic, but is unable to work when the button is programed as a Response? If the keypad key buttons are working then it cannot be a RS485 or communications problem, it can only be due to the Response numbers not matching between the KT03 and Comfort. If the KT03 button is maped to a Response and you modify the Responses itmay cause the Response numbers to change, and KT03 points to the wring response number, even though you did not change anything on the KT03 Can you run the Bus Monitor from Tools, press Start to start it Load the cclx file that you send 2015.cclx and write to Comfort and KT03 Then go to the KT03 and press just the button for Lights Lower Hall in your cclx file. This activates the Response LHTime1 (response 26). Halt the Bus Monitor, Save All and send the saved file. This will show what Response is being called by KT03
|
||||||||||||
|