The positions of the shunts for ID setting for 5 Slaves  is shown in the revised SEM Manual see http://www.cytech.biz/sem_manual.html
The picture below shows the shunts setting

You do not need to disconnect the Slaves while doing the ID setting. Just change the shunt on each one according to the table

Reset each Slave and Comfort when you have finished changing the IDs

Make sure that the Slave numbering is consecutive ie you do not have any gaps in the ID