When the system is armed to Night mode, motion detectors may be active. This may cause false alarms when people forget to disarm the system when moving around the house It is possible to start an entry delay in Night mode when the detector is triggered so giving users a chance to disarm the system In the Zone Response of the detector assign a Response as follows; If Security Mode = Night Mode Start Entry Delay Endif --------------------------------------------------------------------------------------- Another application is in Night Mode, opening a window will cause an alarm People often forget that the system is armed, and open the window causing an alarm It is possible to start an entry delay when an internal motion detector has been triggered first The Motion Detector Response is programmed as follows If SecurityMode = NightMode Then Do NullResponse After 30 Seconds Using nightWindowTimer End If This starts a timer for 30 seconds. During the 30 seconds opening the window is programmed to start entry delay The window Zone Response is programmed as folows; If Timer nightWindowTimer <> 0 Then Start EntryDelay End If This starts an entry delay only if the nightWindowTimer is running Change Entry Delay can be placed before Start entry delay to use a different entry delay than the normal entry delay Last edited on Wednesday Dec 24th, 2014 10:08 am by |
|||||||||
|