There were several problems with the cclx file that you sent
  1. The UCM/Cbus ID is 4, there is no UCM with ID=3 and presumably the number of UCMs in Comfort is less than 4, so the UCM/Cbus was not polled
  2. The Cbus application in the Cbus commands sent to Cbus were changed from Lighting (56) to other unused applications
  3. The commands only turn on the lighting, and none to turn off the lighting so after the above problems are fixed, there may be no responses to turn off the lights
Please download the UCM/Cbus manual from http://www.cytech.biz/ucmcbus_manual.html for a full understanding of operation and programming of UCM/Cbus

Let us know if you have any more problems