BUSY2 remaining on means that the UCM is not getting an acknowledge reply from the bus when it sends a mesage
Could there be a conflict in the Physical address?

Your UCM/KNX is firmware 5.234 from checking the serial number
If possible please upgrade to KNX 6.015 which is the latest, so that we can check according to the same version

Could it possible that the KNX Bus  has a problem?

It is also possible that the KNX submodule  is faulty but we should check the firmware first

By the way I am moving this post from the UCM Troubleshooting to the KNX forum so it will be easier to find