agenor
|
Greetings, we are having problems with the UCM/KNX module. Some parts of the system (family house) such as lighting control, gate control, garage door control, etc., are controlled by Cytech alarm module. The system was working well for about a month. Then suddenly the system stopped working, for example, the garage door would not close/open or a light controlled by Cytech would not turn On or Off when pressing the appropriate KNX push button in the house. After a while the system started working again on its own. Also, the system would start working again after pressing the RESET button on the UCM/KNX module. This happened so far a couple of times. When this problem occurred, the status of the LED-s on the UCM/KNX module were: RDY - steady ON BUSY1 - OFF, but when pressing a KNX push button it would blink once BUSY2 - steady ON ERR - OFF, but when pressing a KNX push button it would blink once The EVENT LOG in Comfigurator (v. 3.4.4.0) did not show anything odd. When the system was not working we tried the MONITOR MODE function in Comfigurator. Even though the system was not responding after pressing the push buttons, MONITOR mode showed the source physical KNX address of the push button that sent the KNX telegram to Cytech. We are using this UCM/KNX module: UCM PC01-066A (Big PCB - Primary module), Bar code: C032275 PC01-035B (Small PCB - EIB module), Bar code: P046747
|
|||||||||
|