The problem is most likely not related to the error in the uploaded file
That difference in the uploaded is most likely due to a conversion error by Comfigurator when it reads the file
If possible use the latest 3.5.1 (beta) to read the file again and see if this still happens.

The intermittent problem with KNX may be related to the bus
When the error occurs what are the state of the LEDs on the UCM/KNX? Is the ERR led on or any of the BUSY1 and BUSY2? If ERR led is on it indicates a problem with the KNX bus, perhaps voltage or some corruption on the bus. The normal condition of the LEDs on UCM/KNX is RDY led ON, ERR odd, BUSY1 blinks when there is a telegram from the bus and BUSY2 blinks when there is a telegram to the Bus from Comfort