Most likely the CBUS will be UCM 2

I think it may be time for an upgrade...

Not only is the hard ware out of date as is the firmware but you will be using the old comfigurator.ccl files.

There are a number of things that you can do.
- Reload the last software you uploaded (if you still have a copy)use Comfigurator 3.4.4
- Check the connections the CBUS UCM - Have you used CBUS cable to get back to the CBUS bus? does the cable travel next to any mains cables.
- What type of light fittings does the CBUS have after a while mains transformers degrade and the capacitive value alters. This can cause interference on the CBus bus (YES IT CAN)so try carrying out the operation with all CBUS light fully on and then fully off. A yes Palmlodge this nay be your problem as well - do you have mains downlighters?

I have more but that will do for now !