View single post by slychiu
 Posted: Friday May 18th, 2012 03:06 am
 PM  Quote  Reply  Full Topic 
slychiu



Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

2 Comforts with UCM/Cbus can be connected to the same Cbus network as long as their Unit addresses are diferent (this is set by the Cbus Toolkit)
Each Comfort can send messages to Cbus and will receive messages from Cbus mapped to counters. The counter responses of each Comfort must be programmed to respond to the appropriate group addresses

However using the Security application will cause a problem because Cbus assumes there is only one security system in the network. Hence if you arm through Cbus, both systems will be armed. When each system is armed by its own keypad then the status of the security on the Cbus Touchscreen will be updated to the latest security status message from one of the systems

In conclusion, it is better not to use the security application with 2 Comforts

 Close Window