2 Comforts with UCM/Cbus can be connected to the same Cbus network as long as their Unit addresses are diferent (this is set by the Cbus Toolkit) Each Comfort can send messages to Cbus and will receive messages from Cbus mapped to counters. The counter responses of each Comfort must be programmed to respond to the appropriate group addresses However using the Security application will cause a problem because Cbus assumes there is only one security system in the network. Hence if you arm through Cbus, both systems will be armed. When each system is armed by its own keypad then the status of the security on the Cbus Touchscreen will be updated to the latest security status message from one of the systems In conclusion, it is better not to use the security application with 2 Comforts
|
||||||||||||
|