Threads: 5
Hello again,
What is actually EOL, what is the purpose and how does it work. And how to wired it.
Thanks,
Regard
salizam
08-10-2007, 05:10 AM
(This post was last modified: 09-04-2010, 06:58 AM by slychiu.)
EOL means End of Line Resistor These are the resistor values which must be connected to the sensor contact when the Zone shunts are set to the End of Line position, ie away from the terminal block. End of Line Resistors allow Comfort to raise a Trouble alarm when the alarm wiring is cut
You can refer to the installation manual for information on how to connect the resistors.
Threads: 885
Comfort\'s End of Line Resistor values are 2.7K ohms in series with the contact and 4.7 K ohms in parallel with the contact.
The 2.7K ohms value can be substituted with 2.2 Kohms without any problem.
The values 2.2 Kohm and 4.7Kohm are commonly used in the UK and some other countries. If Comfort is bneing installed to replace another alarm system with these values, then the EOL resistors need not be changed
Threads: 18
A question concerning testing circuits with two end of line resistors.
As I understand it, normally the alarm expects to see 2K7 ohms.
When the sensor is activated it sees 2700 + 4700 or 7400 ohms and raises the alarm type.
What are the tolerances involved? In other words, its not 2700 exactly or 7400 exactly, but some range of values which averages at these.
I ask this because in periodically maintaining the wiring and associated sensor circuits I would like to know when its timely to anticipate problems and tighten up connections / replace sensors on those circuits.
Thanks in advance.
Threads: 476
1 K difference should still work
Threads: 1
good morning !
i just wanna ask how to compute the end of line resistor in fire alarm ?
Threads: 885
For comfort, you need 2.2K in series and 4.7 K in parallel
Fire alarms may not be compatible with comfort. most of them are 24V
You need to use 12V smoke or heat detectors for comfort