Comfort Automation/ Security System Forums
SEM IDs - Printable Version

+- Comfort Automation/ Security System Forums (https://www.comfortforums.com)
+-- Forum: Products (https://www.comfortforums.com/forum-3.html)
+--- Forum: Expansion Modules (https://www.comfortforums.com/forum-91.html)
+--- Thread: SEM IDs (/thread-3786.html)



- intelilar - 04-23-2014

Hello

How should i adress the SEM

I have 4 jumpers (ABCD)

Can anyone tell me wich are the positions of the jumpers for adressing 5 SEM?

Should i adress one by one, having the other disconected, or can i have all of them with power and simply change the jumpers.

Any procedure?

Regards



- ident - 04-24-2014

The positions of the shunts for ID setting for 5 Slaves  is shown in the revised SEM Manual see https://www.cytech.biz/sem_manual.html
The picture below shows the shunts setting

You do not need to disconnect the Slaves while doing the ID setting. Just change the shunt on each one according to the table

Reset each Slave and Comfort when you have finished changing the IDs

Make sure that the Slave numbering is consecutive ie you do not have any gaps in the ID