Velbus died?
 Posted: Saturday Nov 16th, 2013 03:36 pm
steefdebruijn
Tried to write some data to velbus EEPROM and received errors doing so. Scanning all modules indicates Velbus is not found. Led is green, sometimes all D2,3,4 leds blink red.
Is it broke?
Steef
 Posted: Sunday Nov 17th, 2013 12:48 am
Does the D9 red led remain off? If so, this looks like a problem with incorrect UCM/Velbus ID
Check the ID shunts, set to ID=2 (or 3 if ID 2 is taken up), Scan again and see if Comfigurator can find the module. Then do write to Comfort
If the UCM/Velbus is polled both D9 and D10  will blink
 Posted: Sunday Nov 17th, 2013 07:36 am
steefdebruijn
I did not change ID settings but double-checked anyway. It is correctly set at ID 4. It has worked fine for the past couple of weeks but stopped responding after trying to write configuration to EEPROM. All other UCM's working fine (ZWave, Ethernet, GSM)
LED indicators:
D1 (green) is permanent ON, only flickers OFF once for a quarter of a second every ten seconds or so right after the three red's go OFF (see below)
D2,3,4 (red) are permanently OFF, only flash for a second every ten seconds or so.
D9 (red) is permanently OFF
D10 (green) is more or less permanently ON (somewhat flickering)
D11 (green) is OFF, but sometimes gives a very short flicker (less than a quarter of a second)
D12 (red) is OFF
Did it fry on EEPROM write?
Steef
 Posted: Sunday Nov 17th, 2013 07:41 am
steefdebruijn
Additional info:
Velbus firmware sticker is 6.011, upgraded to 7.006 couple of weeks ago.
Just reloaded firmware through UCM Firmware programming cable. Went OK but after reconnecting the UCM it is still not found by Comfort.
Steef
 Posted: Sunday Nov 17th, 2013 08:37 am
I suspect something in the eeprom is causing the UCM/Velbus to reset itself every 10 seconds.
Try removing the eeprom from U2(after power off)
Alsouse another eeprom in U2 if possible
 Posted: Sunday Nov 17th, 2013 08:49 am
steefdebruijn
Additional info
Pulled the EEPROM from the board and reconnected the UCM. D4 is now flashing (for the missing EEPROM of course) but the Confort scan now says 'not polled'. That seems to me better than 'not found'.
After writing config to comfort rescan states Velbus UCM is polled. Version=7.006, latest=6.011.
After reinserting the EEPROM and reconnecting the UCM, it is back to the faulty behavior stated above.
Steef
 Posted: Sunday Nov 17th, 2013 09:02 am
The eeprom may have gone faulty, but write to eeprom should not have caused this as that only erases data and writes into the eeprom
Try another eeprom eg the "spare " eeprom in the UCM/USB or ethernet in U2 used for backup, see if that fixes the problem
You can buy another eeprom from the distributor or elsewhere (24C256)
 Posted: Sunday Nov 17th, 2013 09:24 am
steefdebruijn
Thx for the info. Found an online shop selling the 24LC256 I/P.
Can i just pull the EEPROM from the Eth UCM? I have only one installed in the U2 socket. (U3 is empty)
Steef
 Posted: Sunday Nov 17th, 2013 09:34 am
yes you can use the U2 from UCM for testing to verify that it works in the Velbus
 Posted: Thursday Nov 21st, 2013 06:24 pm
steefdebruijn
Inserted a brand new EEPROM and the thingie was back to life. Earlier programmed responses to write to velbus (switch lamp) worked OK.
But... Changing the Velbus to Comfort tab and writing to EEPROM went OK but the thing died again on me. Exactly the same symptoms described earlier.
So the EEPROM write does some serious harm in some way.
Any ideas?
Steef
 Posted: Friday Nov 22nd, 2013 01:14 am
Can you send your cclx file to support@cytech.niz so we can try to duplicate thank
 Posted: Tuesday Nov 26th, 2013 12:24 pm
We have confirmed that there is a bug in Velbus 7.006
This happens if Send Date and Time to Velbus is checked and Modules VMB4PD OR VMB1TC are in Velbus to Comfort Tab
The UCM/Velbus does not like what is in the EEPROM, but the EEPROM is not dead. When the bug is fixed it will come alive again
We are doing the fix and will release the update soon
Thanks for the fedback
 Posted: Wednesday Nov 27th, 2013 11:03 am
13th Post
steefdebruijn
I can confirm that the Firmware update to 7.007 fixes the problem.
Steef
 Current time is 03:13 pm