Howser
I have an input connected to a ISM07 submodule that I have configured as RIO Input and have setup on/off responses  (SCS/RIO).
I have a need to use this input as an alarm input, and I cannot physically wire this, so I thought of using one of the alarm inputs as a virtual input.
What would be the ideal way of doing this?
  1.  Change the input from RIO Input to Virtual Input on the ISM07? Would I still need to flag the alarm input as virtual?
  2. Add actions (Virtual Input on and off) to the existing responses and set the flag of the alarm input as virtual?
Setup:
  • Comfort Model: CM9001-ULT
  • Comfort Version 8.005
  • ScsRio (IRIO) Version 7.024
 Posted: Monday Sep 9th, 2024 11:58 am
yes make the IRIO input a virtual input mapped to an unused zone on comfort. The comfort input would automatically becine a virtual input and you can use its on and off responses
 Posted: Tuesday Sep 10th, 2024 05:14 pm
Howser
I have done that, thanks.
I have set this input as an Entry Path, but it triggers the alarm immediately.
 Posted: Wednesday Sep 11th, 2024 12:58 am
can you send the cclx file to support@cytech/biz?
 Posted: Thursday Sep 12th, 2024 08:36 am
Howser
Done.
 Posted: Monday Sep 16th, 2024 03:14 pm
I suspect it's because it's working as a N/O switch instead of a N/C switch. Setting the Zone Type to either Digital N/O or Digital N/C makes no difference.
This is a tricky one as you can't seem to change the behavior for Active/Inactive states unless you have a Door switch that is N/O by default - which I don't think is a good idea.
The other problem is that on reset it doesn't update the virtual zone state to what the iRIO has detected which is undesirable. (testing with iRIO with 7.027).
 Posted: Tuesday Sep 17th, 2024 01:39 am
N/O or N/C does not make any difference for Zone Trouble. Zone Trouble is caused by wiring problems or mismatch between Zone shunts settings and EOL resistors eg if you have the zone shunts set to to EOL and you have EOL resistors on the zone or vice versa.
Your event log shows that you have zone trouble on zones 14 to 16 ie the LEM connected to Comfort.  You say that this is LEM01B without any shunts.  To test these zones, remove all the wires from zones 14 to 16, then use a short wire to short and open the zones and check if this causes zone trouble. If zone trouble occurs without any wires then it is due to a fault in the LEM01B. If there is no zone trouble then it is a fault in the wiring
The LEM on Slave 2 is an old LEM01-M2 without shunts so it cannot be used with SEM01C without EOL shunts
 Posted: Tuesday Sep 17th, 2024 09:29 pm
Howser
The challenge is that these zones do not always report Zone Trouble. I have to figure out what conditions do.
 Posted: Wednesday Sep 18th, 2024 01:38 am
If you have used the short/open method of testing the zones, and they do not report zone trouble, then tou can eliminate the LEM01 as the cause of the problem
 Posted: Thursday Sep 19th, 2024 10:54 am
Howser
When I test each LEM with short/open they do not report zone trouble.
 Posted: Thursday Sep 19th, 2024 11:07 am
Howser
However at times when input 95 or 96  detects motion at the same time that the inputs on the LEM are shorted, then zone trouble is announced.
 Posted: Friday Sep 20th, 2024 01:21 am
can you change the viruial inputs from 95 and 96 to another unused zone eg   zone 65 and 66. does the zone trouble change
 Posted: Friday Sep 20th, 2024 04:42 am
13th Post
If you have the latest firmware and Comfigurator, you can trigger virtual inputs on and off using I! in Comfigurator.  eg  I!6001 Input 96 On,  I!6000 Input 96 Off I!5F01 Input 95 On
I!5F00 Input 95 Off
You can test this with Zones 14 to 16 in on and off state. i could not find any instnace of zone trouble
 Posted: Friday Sep 20th, 2024 12:20 pm
14th Post
Howser
Investigation 1
Zone trouble is still happening.
09/20 13:58 Alarm Type # ZoneTrouble (5)
09/20 13:58 Zone Trouble # XXXXXXX_PIR (16)
Investigation 2
If you have the latest firmware and Comfigurator, you can trigger virtual inputs on and off using I! in Comfigurator.  eg  I!6001 Input 96 On,  I!6000 Input 96 Off I!5F01 Input 95 On I!5F00 Input 95 Off
I tested this and once the virtual Input is active, then I get Zone trouble when the PIRs are triggered. But, it only reports the zone trouble once for each active cycle, no matter how long I keep the virtual input active for.
 Posted: Monday Sep 23rd, 2024 04:54 am
15th Post
We found a bug in handling of LEM zones, but not sure if it is to do with your particulr problem. Can you upgrade to ULTA 8.008 using this link http://www.cytech.biz/download_files.php?item_id=1415
However from your cclx file your 1st ucm is 7.150. Please upgrade to the latest version otherwise you will not be able to do the upgrade to the Ultra comfort firmware
Let me know if you still have the zone trouble problem
 Posted: Monday Sep 23rd, 2024 01:21 pm
16th Post
Howser
I tried upgrading the first UCM to 7.225, downloaded the local file, started the upgrade.
 After completing the upgrade the version on Comfigurator is still showing 7.150.
Below is Comfort Version screenshot.
 Posted: Tuesday Sep 24th, 2024 01:15 am
17th Post
Your screenshot shows you are upgrading the UCM firmware to 7.225, but you also have to upgrade the Controller to 8.008 next.  In short there are 2 upgrade operations, UCM, then Controller
 Posted: Tuesday Sep 24th, 2024 06:37 pm
18th Post
Howser
The UCM did not upgrade, the upgrade process went through, but it still shows version 7.150.
 Posted: Wednesday Sep 25th, 2024 01:25 am
19th Post
sorry I misunderstood your previous email, You completed the UCM upgrade to 7,225 without error but the version is still 7.150?
Did you right click on the UCM and select Check for Firmware upgrades as in the image below?
If the upgrade completes without errors, then you have top scan for modules again to show the updated firmware version
 Posted: Wednesday Sep 25th, 2024 05:57 am
20th Post
Howser
That option is not available
Yes, I scanned for module after Comfigurator showed that the firmware was upgraded.