Comfort Automation/ Security System Forums > Support > Questions on Programming Comfort > External lights with multiple detectors AND function
 Posted: Thursday May 22nd, 2014 02:08 pm
Pharris14
Hi I am trying to configure the following which seems to be how the perimeter function works but I need it to control lights.
1. It is dark
2. A motion detector starts a timer
3. If a second motion detector is triggered this will turn on the floodlights for a period
4. If no second detector is seen then the timer expires
5. If the first detector is re-triggered within the time period then this will not activate the floodlights
Can anyone help please?
 Posted: Thursday May 22nd, 2014 04:12 pm
This is a prime example of logic that can be achieved by Comfort,  which most other systems are not able to do, at least in this price range
Rather than just giving the solution, we will offer a free UCM of any type to the first person who can give a solution to this problem which works for Pharris14
 Posted: Sunday May 25th, 2014 10:19 am
Pharris14
Hi Ident, I have found a way but it may be a bit messy, as follows:
1. Create a response for each detector which sets a flag and calls the "floodlights on" response.2. Floodlights on response does a non zero AND test on the flags then turns the floodlight output on3. Turn the floodlight timer off after 35 seconds4. Resets the flags (I have only used two detectors to start with).
"floodlights on"Flag ExtPir1 <> 0 And Flag ExtPir2 <> 0 Then    Do Lounge2WaySwOn    Do Lounge2WaySwOff After 35 Seconds Using Timer02    Do ExtPir2FlagReset After 30 Seconds Using Timer16    Do ExtPir1FlagReset After 30 Seconds Using Timer15End If
What do you think?
Thanks...
 Posted: Sunday May 25th, 2014 11:06 am
You can do it more simply that that
This is the 1st Motion Detector Zone Response:
If NightTime <> 0 Then
    Do NullResponse After 30 Seconds Using Timer01
End If
This starts a timer if the Night Time Flag is on (set by sunset). You can use other logic or sensors to determine when it is dark
Do Null Response means it does nothing if the timer expires
If the motion detector is triggered again the timer is restarted
This is the 2nd Motion detector Response
If Timer Timer01 <> 0 Then
    Do Floodlights On
    Do Floodlights Off After 50 Seconds Using Timer02
End If
That means if Timer 1 is running ie it is still within the delay caused by the 1st motion detector triggered, then turn on the lights for 50 seconds in the example
 Current time is 07:17 am
