You can use the UCM/232 (formerly UCM05), UCM/USB or UCM/Ethernet to upgrade firmware of any type of UCM with Flash firmware. The UCM used to do the upgrade must be minimum firmware 5.178. Note that this procedure applies to upgrading the Slave (SEM) firmware although the picture shows a UCM being upgraded.
The connections between the UCM used to do the upgrade and the UCM being upgraded are shown in the picture below. The UCM/USB is shown in the picture (ignore the RS232 connector shown)
The procedure to upgrade UCM or Slave firmware is shown here. For instructions on how to upgrade Comfort firmware, go to http://www.comfortforums.com/view_topic.php?id=1216&forum_id=4&jump_to=4472#p4472
The UCM doing the upgrading (shown on the left) is connected to the UCM being upgraded (shown on the right) via a Programming Cable which comes with every UCM/232, UCM/USB or UCM/Ethernet. The programming cable is a split cable with two connectors (6 pin and 2 pin) on one end and a single 6 pin connector on the other end
 - Connect the cable with the two ends to the programming UCM (PP1 and PP3) and the end with a single connector to the PP1 on UCM to be upgraded. PP1 is a 6 way header and PP2 is a 2 way header. The connection is shown in the picture below.
- On the UCM to be upgraded, insert a shunt on the PP2 header. In the picture, PP2 can be seen below the green (D10) and red (D9) leds on the UCM being upgraded.
- The UCM being upgraded should not be connected to Comfort, the only connection is to the UCM doing the upgrade via the programming cable. When the connection is made, the red (D9) and green (D10) leds on the UCM being programmed will flash, with D9 (red) very fast so it appears steady and D10 (green) at a slower rate.
- Run Comfigurator, go to menu Options > UCM Interface and select USB, Serial or Ethernet and the appropriate port in the usual way.
- Go to Transfer > Firmware Upgrade.. Browse to select the firmware file with extension .cbf for the UCM to be upgraded.
- The firmware upgrade files can be downloaded from http://www.cytech.biz/upgrades.html
- When selected, the firmware upgrade will start, and will take only a minute for a UCM. The progress bar will show the completion rate of the upgrade. If the upgrade process fails or halts for any reason, just repeat the transfer > Firmware upgrade process.
- When it has completed successfully, remove the cable from the UCM being upgraded and the other UCM. Also remove PP2 shunt from the UCM being upgraded.
If you have upgraded a Slave, UCM/KNX, UCM/CBUS, UCM/GSM2, etc the firmware version can be checked using Comfigurator 3.1.3 and above via the Scan Modules function in the Modules Tab
If you have two UCMs (UCM232, UCM/USB or UCM/Ethernet), one can upgrade the other, and the connections can be reversed so the other can be upgraded. a UCM cannot upgrade its own firmware
Please note that only firmware of the same type can be used to upgrade a module. For example, Comfort Ii Ultra can only be upgraded with Comfort II Ultra firmware, Slave SEM can only be upgraded with Slave firmware. UCM/232, USB and Ethernet share the same firmware. UCM/KNX, UCM/Cbus have their own tyoe of firmware so only the same firmware type can be used to upgrade the respective UCMs. eh UCM/KNX firmware cannot be used to upgarde UCM/Cbus or UCM/232, USB or Ethernet.
Attachment: CIMG0425 small.jpg (Downloaded 58 times) Last edited on Monday Jul 5th, 2010 01:59 am by slychiu
|
|
|
| Posted: Saturday Apr 3rd, 2010 04:59 pm |
|
2nd Post |
mikegriff
Member
| Joined: | Saturday Aug 19th, 2006 |
| Location: | United Kingdom |
| Posts: | 15 |
| Status: |
Offline
|
|
If I am just upgrading a UCM does the UCM that is doing the upgrading need to be connected to the comfort motherboard or can I just feed the 12v?
thanks
Mike
|
|
|
| Posted: Sunday Apr 4th, 2010 02:27 am |
|
3rd Post |
ident
Administrator

| Joined: | Wednesday Aug 9th, 2006 |
| Location: | Singapore |
| Posts: | 587 |
| Status: |
Offline
|
|
You only need to connect the 12V to the UCM doing the upgrading. The KA/KB or data does not need to be connected. However it may be convenient to leave in place the white 4 way cable between the UCM and Comfort.
The UCM being upgraded need not be connected at all except by the 6 way programming cable
|
|
|
| Posted: Tuesday Apr 13th, 2010 03:52 pm |
|
4th Post |
dcrera
Comfort Installers
| Joined: | Monday Aug 7th, 2006 |
| Location: | South Africa |
| Posts: | 203 |
| Status: |
Offline
|
|
Resolved
Last edited on Tuesday Apr 13th, 2010 07:05 pm by dcrera
|
|
|