Hi,
I have CBus and Comfort units installed
I am able to communicate Comfort to CBus using UCM to CBus Module (Firmware v. - 7.068) and able to trigger CBus group address using comfort
But What I want is to use CBus group address to trigger comfort IR1Output1 response to switch on my AC
Please describe if it is possible.
Thankyou
|
Posted: Wednesday Jan 4th, 2017 04:30 pm |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5498 |
Status: |
Offline
|
back to top
|
In the Cbus to Comfort tab, you can map Cbus Lighting application group addresses to Comfort Counters eg Group address 1 to Counter 10
Group address 1 turned on will set Counter 10 to 255
Group address 1 turned off will set Counter 10 to 00
Each Counter can be asigned to Counter Response
The counter Response can be programed to send Off and On IR signals to the Aircon
This is explained in UCM/Cbus2 Manual which can be downloaded rfrom http://www.cytech.biz/ucmcbus2_manual.html
Do remember to Write To Comfort, AND write to EEPROM in Cbus 2 tab in order for the program to work
You should also use Current sensors to monitor the state of the Aircon fan coil, This gives an On/Off status to the Comfort Input
In The Physical Inputs Tab in Cbus you can map each Comfort Input to a Cbus Lighting group address
Thus when the aircon is turned on, the zone sends its status to the cbus group address so the Cbus switch status follows the actual state of the aircon, even if the aircon is conttrolled by the handheld remote control
|
Posted: Wednesday Jan 4th, 2017 05:34 pm |
|
3rd Post |
Posted: Thursday Jan 5th, 2017 11:18 am |
|
4th Post |
RahulPandey686
Member
Joined: | Thursday Jul 21st, 2016 |
Location: | |
Posts: | 18 |
Status: |
Offline
|
back to top
|
Done it successfully
Thanks
|
|